6ES7 318-3EL01-0AB0
General information
Hardware product version
01
Firmware version
V3.2
Supply voltage
24 V DC
Yes
permissible range, lower limit (DC)
19.2 V
permissible range, upper limit (DC)
28.8 V
Mains buffering
- Mains/voltage failure stored energy time
5 ms
1 s
Input current
Current consumption (rated value)
1 250 mA
Current consumption (in no-load operation), typ.
500 mA
Inrush current, typ.
4 A
I²t
1.2 A²·s
Power losses
Power loss, typ.
14 W
Memory
Type of memory
other
Work memory
2 048 kbyte
No
- Size of retentive memory for retentive data blocks
700 kbyte
Load memory
Yes
8 Mbyte
- Data management on MMC (after last programming), min.
10 a
Backup
Yes
Yes
CPU processing times
for bit operations, typ.
0.004 µs
for word operations, typ.
0.01 µs
for fixed point arithmetic, typ.
0.01 µs
for floating point arithmetic, typ.
0.04 µs
CPU-blocks
Number of blocks (total)
4 096; (DBs, FCs, FBs); the maximum number of loadable blocks can be reduced by the MMC used.
DB
4 096
64 kbyte
FB
4 096
64 kbyte
FC
4 096; Number range: 0 to 7999
64 kbyte
OB
64 kbyte
1
1
- Number of delay alarm OBs
2
- Number of time interrupt OBs
4
- Number of process alarm OBs
1
3; OB 55, 56, 57
- Number isochronous mode OBs
1; OB 61
1
- Number of asynchronous error OBs
6
- Number of synchronous error OBs
2
Nesting depth
16
- additional within an error OB
4
Counters, timers and their retentivity
S7 counter
2 048
Yes
0
2 047
Z 0 to Z 7
Yes
0
999
IEC counter
Yes
SFB
Unlimited (limited only by RAM capacity)
S7 times
2 048
Yes
0
2 047
No retentivity
10 ms
9 990 s
IEC timer
Yes
SFB
Data areas and their retentivity
retentive data area, total
All, max. 700 KB
Flag
8 192 byte
Yes; from MB 0 to MB 8191
MB 0 to MB 15
8; 1 memory byte
Data blocks
4 096; Number range: 1 to 16000
64 kbyte
Yes; via non-retain property on DB
Yes
Local data
32 768 byte; Max. 2048 bytes per block
Address area
I/O address area
8 192 byte
8 192 byte
8 192 byte
8 192 byte
Process image
8 192 byte
8 192 byte
8 192 byte
8 192 byte
256 byte
256 byte
Subprocess images
- Number of subprocess images, max.
1; With PROFINET IO, the length of the user data is limited to 1600 bytes
Digital channels
65 536
65 536
1 024
- Outputs, of which central
1 024
Analog channels
4 096
4 096
256
256
Hardware configuration
Number of DP masters
2
4
Number of operable FMs and CPs (recommended)
8
8
Rack
4
8
Time of day
Clock
- Hardware clock (real-time clock)
Yes
- battery-backed and synchronizable
Yes
10 s; Typ.: 2 s
6 wk; At 40 °C ambient temperature
- Behavior of the clock following POWER-ON
Clock continues running after POWER OFF
- Behavior of the clock following expiry of backup period
Clock continues to run with the time at which the power failure occurred
Operating hours counter
4
0 to 3
0 to 2^31 hours (when using SFC 101)
1 hour
Yes; Must be restarted at each restart
Clock synchronization
Yes
Yes
Yes
Yes; With DP slave only slave clock
Yes
Yes
Yes
Yes; as client
Digital inputs
Number of digital inputs
0
Digital outputs
Number of digital outputs
0
Analog inputs
Number of analog inputs
0
Analog outputs
Number of analog outputs
0
Interfaces
Number of USB interfaces
0
Number of parallel interfaces
0
Number of 20 mA interfaces (TTY)
0
Number of RS 232 interfaces
0
Number of RS 422 interfaces
0
Number of other interfaces
1; Ethernet, 2-port switch, 2*RJ45
1st interface
Interface type
Integrated RS 485 interface
Physics
RS 485
Isolated
Yes
Power supply to interface (15 to 30 V DC), max.
150 mA
Functionality
Yes
Yes
Yes; A DP slave at both interfaces simultaneously is not possible
- Point-to-point connection
No
MPI
12 Mbit/s
Yes
Yes
- Global data communication
Yes
Yes
Yes
- S7 communication, as client
No; but via CP and loadable FB
- S7 communication, as server
Yes
DP master
12 Mbit/s
- Number of DP slaves, max.
124
Yes
Yes
No
Yes; I blocks only
Yes
No
Yes
- Equidistance mode support
Yes
No
Yes
- Activation/deactivation of DP slaves
Yes
- Number of DP slaves that can be simultaneously activated/deactivated, max.
8
- Direct data exchange (slave-to-slave communication)
Yes; As subscriber
Yes
8 kbyte
8 kbyte
244 byte
244 byte
DP slave
12 Mbit/s
- Automatic baud rate search
Yes; only with passive interface
32
- User data per address area, max.
32 byte
Yes
Yes; with interface active
No
No
Yes
No
Yes; Connection configured on one side only
Yes
No
244 byte
244 byte
2nd interface
Interface type
Physics
RS 485
Isolated
Yes
200 mA
Functionality
No
Yes
No
No
No
No
No
DP master
12 Mbit/s
124
Yes
Yes
No
Yes; I blocks only
Yes
No
Yes
Yes; OB 61 - isochronous mode is possible either on DP or PROFINET IO (not simultaneously)
Yes
Yes
8
Yes; As subscriber
Yes
8 kbyte
8 kbyte
244 byte
244 byte
DP slave
The latest GSD file is available at: http://www.siemens.de/profibus-gsd
12 Mbit/s
32
32 byte
Yes
No
No
Yes
No
Yes
No
244 byte
244 byte
3rd interface
Interface type
PROFINET
Physics
Ethernet RJ45
Isolated
Yes
Integrated switch
Yes
Number of ports
2
Automatic detection of transmission speed
Yes; 10/100 Mbit/s
Autonegotiation
Yes
Autocrossing
Yes
Change of IP address at runtime, supported
Yes
Media redundancy
Yes
- Switchover time on line break, typically
200 ms; PROFINET MRP
- Number of stations in the ring, max.
50
Functionality
No
No
No
Yes; Also simultaneously with I-Device functionality
Yes; Also simultaneously with IO Controller functionality
Yes
Yes; Via TCP/IP, ISO on TCP, and UDP
Yes
5
PROFINET IO Controller
100 Mbit/s
- Number of connectable IO devices, max.
256
- Max. number of connectable IO devices for RT
256
256
- Number of IO devices with IRT and the option "high flexibility"
256
61
- Number of IO Devices with IRT and the option "high performance", max.
64
64
Yes
- Prioritized startup supported
Yes
- Number of IO Devices, max.
32
- Activation/deactivation of IO Devices
Yes
- Maximum number of IO devices that can be activated/deactivated at the same time.
8
- IO Devices changing during operation (partner ports), supported
Yes
- Max. number of IO devices per tool
8
- Device replacement without swap medium
Yes
250 μs, 500 μs,1 ms; 2 ms, 4 ms (not in the case of IRT with "high flexibility" option)
250 µs to 512 ms (depending on the operating mode, see Manual "S7-300 CPU 31xC and CPU 31x, Technical Data" for more details)
Yes
Yes
Yes; with loadable FBs, max. configurable connections: 16, max. number of instances: 32
8 kbyte
8 kbyte
- User data consistency, max.
1 024 byte
PROFINET IO Device
Yes
Yes
No
Yes
Yes; With SFB 73 / 74 prepared for loadable PROFIenergy standard FB for I-Device
Yes
- Number of IO controllers with shared device, max.
2
1 440 byte; Per IO Controller with shared device
64
- User data per submodule, max.
1 024 byte
PROFINET CBA
Yes
Yes
Open IE communication
- Open IE communication, supported
Yes
- Number of connections, max.
32
- Local port numbers used at the system end
0, 20, 21, 23, 25, 80, 102, 135, 161, 443, 8080, 34962, 34963, 34964, 65532, 65533, 65534, 65535
- Keep-alive function, supported
Yes
Isochronous mode
Isochronous operation (application synchronized up to terminal)
Yes; Via 2nd PROFIBUS DP or PROFINET interface
Communication functions
PG/OP communication
Yes
Data record routing
Yes
Yes
8
- Number of GD packets, max.
8
- Number of GD packets, transmitter, max.
8
- Number of GD packets, receiver, max.
8
22 byte
- Size of GD packet (of which consistent), max.
22 byte
S7 basic communication
Yes
76 byte
- User data per job (of which consistent), max.
76 byte; 76 bytes (with X_SEND or X_RCV); 64 bytes (with X_PUT or X_GET as server)
S7 communication
Yes
Yes
Yes
See online help of STEP 7 (shared parameters of the SFBs/FBs and of the SFCs/FCs of S7 Communication)
S5-compatible communication
Yes; via CP and loadable FC
Yes; via integrated PROFINET interface and loadable FBs
32
- Data length for connection type 01H, max.
1 460 byte
- Data length for connection type 11H, max.
32 768 byte
- Several passive connections per port, supported
Yes
32
32 768 byte
32
1 472 byte
Web server
Yes
5
Yes
PROFINET CBA (at set setpoint communication load)
- Setpoint for the CPU communication load
20 %
- Number of remote interconnection partners
32
- Number of functions, master/slave
50
- Total of all Master/Slave connections
3 000
- Data length of all incoming connections master/slave, max.
24 000 byte
- Data length of all outgoing connections master/slave, max.
24 000 byte
- Number of device-internal and PROFIBUS interconnections
1 000
- Data length of device-internal und PROFIBUS interconnections, max.
8 000 byte
- Data length per connection, max.
1 400 byte
- Remote interconnections with acyclic transmission
- Sampling frequency: Sampling time, min.
200 ms
- Number of incoming interconnections
100
- Number of outgoing interconnections
100
- Data length of all incoming interconnections, max.
3 200 byte
- Data length of all outgoing interconnections, max.
3 200 byte
1 400 byte
- Remote interconnections with cyclic transmission
- Transmission frequency: Transmission interval, min.
1 ms
300
300
4 800 byte
4 800 byte
450 byte
- HMI variables via PROFINET (acyclic)
- Number of stations that can log on for HMI variables (PN OPC/iMap)
3; 2x PN OPC/1x iMap
500 ms
600
- Data length of all HMI variables, max.
9 600 byte
- PROFIBUS proxy functionality
Yes
- Number of linked PROFIBUS devices
32
240 byte; Slave-dependent
32
- usable for PG communication
31
- reserved for PG communication
1
- Adjustable for PG communication, min.
1
- Adjustable for PG communication, max.
31
- usable for OP communication
31
- reserved for OP communication
1
- adjustable for OP communication, min.
1
- adjustable for OP communication, max.
31
- usable for S7 basic communication
30
- Reserved for S7 basic communication
0
- adjustable for S7 basic communication, min.
0
- adjustable for S7 basic communication, max.
30
- usable for S7 communication
16
- reserved for S7 communication
0
- Adjustable for S7 communication, min.
0
- Adjustable for S7 communication, max.
16
- Max. total number of instances
32
X1 as MPI: max. 10; X1 as DP master: max. 24; X1 as DP slave (active): max. 14; X2 as DP master: max. 24; X2 as DP slave (active): max. 14; X3 as PROFINET: 48 max.
S7 message functions
Number of login stations for message functions, max.
32; Depending on the configured connections for PG/OP and S7 basic communication
Process diagnostic messages
Yes
simultaneously active Alarm-S blocks, max.
300
Test commissioning functions
Status block
Yes; Up to 2 simultaneously
Single step
Yes
Number of breakpoints
4
Status/control
Yes
Inputs, outputs, memory bits, DB, times, counters
- Number of variables, max.
30
- of which status variables, max.
30
- of which control variables, max.
14
Forcing
Yes
Inputs, outputs
Diagnostic buffer
Yes
500
No
100
- Number of entries readable in RUN, max.
499
Yes; From 10 to 499
Service data
Yes
Ambient conditions
Operating temperature
0 °C
60 °C
Configuration
Configuration software
Yes; V5.5 or higher
programming
see instruction list
8
- System function blocks (SFB)
Yes
Yes
Yes
Yes
Yes
Yes
Yes
Know-how protection
- User program protection/password protection
Yes
Yes; With S7 block Privacy
Dimensions
Width
120 mm
Height
125 mm
Depth
130 mm
Weights
Weight, approx.
1 250 g